AIBOX-K3 (Bianbu 4.0.8, kernel 6.18.3-1.0.0.4): fan spins up to full speed for 1-4 s every 1-3 minutes at idle
Board / kernel: Firefly AIBOX-K3, Firefly Bianbu 4.0.8 image, linux-image-6.18.3-generic 6.18.3-1.0.0.4 (k3/firefly-6.18: cb266e72a599/260924). Fan on the CTF2301 controller, driven by the kernel thermal framework from the thermal_cluster0 zone.
Symptom: sitting idle on the desktop at 36-37 °C, the fan spins up to 2400-5100 rpm for 1-4 seconds every 1-3 minutes, then slows down over a minute and stops, and repeats. Nothing is running; the temperature does not move.
What is happening (from a 1 Hz hwmon log and a kernel thermal trace):
  1. In k3-firefly-common.dtsi the first fan trip of thermal_cluster0 is 35 °C (fan 0-50/255) and the second is 40 °C (fan 64-75). The box idles at 36-37 °C, so the step_wise governor is permanently “throttling” the first trip and every 1 °C flicker of the sensor moves the fan state.
  2. The ctf2301 driver in this kernel truncates the PWM value to the chip’s 46 steps and reports the truncated value back, so step_wise’s +1/-1 steps always end up lower than before. The state ratchets down to 0 in about a minute whichever way the temperature flickers. State 0 writes PWM register 0, which stops the chip’s PWM engine.
  3. At 0, with the trip still throttled, step_wise computes “state - 1” in an unsigned variable, wraps, and clamps to the top of the map (50). Restarting the PWM engine from 0 makes the CTF2301 do a full-speed spin-up pulse. That pulse is the noise. Trace excerpt:
    fan target 45 -> 43  after temp 37->36 (DROPPING)
    fan target 43 -> 39  after temp 36->37 (RAISING)
    fan target  4 -> 1   after temp 36->37 (RAISING)
    fan target  1 -> 50  after temp 37->36 (DROPPING)   <- burst
Already fixed in your tree, not in the shipped kernel: commit d07ff3b789c5 “hwmon: ctf2301: fixed the issue of sudden changes in PWM output” (28 Sep 2026) on k3/firefly-6.18 caches the logical PWM value and never writes PWM 0 in normal operation (idle 8/255). It landed four days after the 6.18.3-1.0.0.4 build, and the driver is built in, so the image still has the bug.
Requests:
  1. Please publish a linux-image-6.18.3-generic build with d07ff3b789c5 for AIBOX-K3 users.
  2. Please revisit the thermal_cluster0 curve: a first fan trip at 35 °C is below this box’s idle temperature. A first trip around 45 °C and a non-zero lower bound on the first cooling map would keep the governor stable even with the old driver.
Workaround I am using until then: a oneshot systemd unit at boot writes 120000 to trip_point_0_temp (parking the only trip whose map starts at 0, which is the one that can ratchet to 0) and 60000 / 62000 / 66000 to trip_point_1_temp / trip_point_2_temp / trip_point_3_temp of the thermal_cluster0 zone (/sys/class/thermal/thermal_zone3 on this image). The fan then stays off at idle and comes on steadily at 25 % from 60 °C. Note that simply raising the first trip (I tried 45 °C) does not help: the trip hysteresis is read-only, and with the fan off the box sits inside the 40-45 °C band, so the kicks just moved there. I have filed the same report with full details on the Firefly-spacemit-linux/linux-6.18 GitHub issue tracker.
Thank you for the detailed report. The issue you described — the fan on AIBOX-K3 repeatedly spinning up while the board is idle at 36–37 °C — has been clearly explained, and we appreciate the hwmon logs, thermal trace, and the reference to commit d07ff3b789c5.
We will forward this to our kernel and SDK team for confirmation, including:
  • whether a new linux-image-6.18.3-generic build containing d07ff3b789c5 can be published for AIBOX-K3;
  • whether the thermal_cluster0 trip points and cooling map should be adjusted, especially given that the current first fan trip at 35 °C is below the typical idle temperature;
  • whether the temporary workaround you shared can be recommended to other users before an official fix is released.